My problem is supplying the rv with enough amps to run. In 120v 1ph, the 5k will supply 52 amps. In 240v 1ph, it will only supply 26 amps. If I wire it with 4 gauge wire from the genny to the rv sub panel and then slit it off to 2 legs, I think I would be getting more amps.

think about what your saying, 26*2=52, there is no more power. the only difference is if the loads are greatly unbalanced and one side pulls more then 26 amps. generally though the big use items are on either side of the panel.

ultimately if you are sure you will never run anything 240, connecting l1 and l2 in the panel together, you would not need to worry about balancing the loads, simply overloading the generator in general
 
Last edited:

Ranger Danger

Member
76
4
8
Location
Vacaville ca
think about what your saying, 26*2=52, there is no more power. the only difference is if the loads are greatly unbalanced and one side pulls more then 26 amps. generally though the big use items are on either side of the panel.

ultimately if you are sure you will never run anything 240, connecting l1 and l2 in the panel together, you would not need to worry about balancing the loads, simply overloading the generator in general

Are you saying that each leg of the 240v would supply 26 amps? If so, you are the first to make that claim and, if you are correct, then my problem does not exist. My understanding is that, in 240 config. I would be getting 26 amps TOTAL.
 

LittleBill

New member
20
0
1
Location
Wilkes Barre / PA
Are you saying that each leg of the 240v would supply 26 amps? If so, you are the first to make that claim and, if you are correct, then my problem does not exist. My understanding is that, in 240 config. I would be getting 26 amps TOTAL.
yes ranger, when you flip the switch to 240, it reverses one of the winding's in the generator head to give you 240v, the wattage does not change, just the amperage per leg, so in 240v you get 26a per leg, or l1(26A) +l2(26A)= 52A total, in 120v single phase mode the winding's are in parallel and the amperage doubles, and the voltage stays the same, thus you get 52 amps at 120v. your rating plate confirms this..
 

98G

Former SSG
Steel Soldiers Supporter
6,160
4,882
113
Location
AZ/KS/MO/OK/NM/NE, varies by the day...
Could be as much as 50 or more. A/c = 16, battery charger = 20, microwave = 12, lights = 5. Now I'm over 50 without trying to hard. I know power management will have to come into play.
50 amps at 120v = 6000 watts. I'd consider that a hard limit.

We were playing with an MEP802 using my plasma cutter. My plasma cutter is 240V 50 amps. Like clockwork, if we turned it past halfway (25 amps @ 240v) the 802 would drop the load.
 

Ranger Danger

Member
76
4
8
Location
Vacaville ca
yes ranger, when you flip the switch to 240, it reverses one of the winding's in the generator head to give you 240v, the wattage does not change, just the amperage per leg, so in 240v you get 26a per leg, or l1(26A) +l2(26A)= 52A total, in 120v single phase mode the winding's are in parallel and the amperage doubles, and the voltage stays the same, thus you get 52 amps at 120v. your rating plate confirms this..
Thank you sir for your assistance (this goes for everybody!!). I am NO electrician, far from it, I am a near complete novice. I must not know how to read the data plate because all I see is that in 120v/240 config, it puts out 26 amps. I dont see anywhere that it says 26 amps per leg.
 

Ranger Danger

Member
76
4
8
Location
Vacaville ca
Ranger, be careful, that 20 amp charger is prolly at 12v DC, not 120v AC. if it pulled 20A AC, it would have to be capable of almost 200A DC ( which is about 1% chance it is).
The charger requires a 20 amp outlet to operate.
Progressive Dynamics model PD9100L
input voltage 105-130 volts 1025 watts
output voltage 14.6 vdc 60 amps
 
Last edited:

LittleBill

New member
20
0
1
Location
Wilkes Barre / PA
The charger requires a 20 amp outlet to operate.
Progressive Dynamics
PD9160ALV 60-AMP
Input Voltage: 105-130 VAC 50/60 Hz 1025 Watts
Output Voltage: 14.6 VDC 60 Amps
Dimensions: 9.15” L x 7.38” W x 3.6” H
Weight: 5.8 lbs.
Have to read the specs. right from your post
Input Voltage: 105-130 VAC 50/60 Hz 1025 Watts

1025/120=8.5A,thus at max load the charger will use about 8.5A, not factoring in power factor(that's another subject)
 
Last edited:

98G

Former SSG
Steel Soldiers Supporter
6,160
4,882
113
Location
AZ/KS/MO/OK/NM/NE, varies by the day...
Your battery charger looks big and bad. I find it plausible it pulls 20 amps of 120v. (Edit - looks more like 10amps, I didn't see the red)

120v x 50 amps = 6000 watts = 240v x 25 amps = just about all that very nice little Lister Petter is going to do.
 
Last edited:

Ranger Danger

Member
76
4
8
Location
Vacaville ca
Your battery charger looks big and bad. I find it plausible it pulls 20 amps of 120v.

120v x 50 amps = 6000 watts = 240v x 25 amps = just about all that very nice little Lister Petter is going to do.
That charger is used for 2 100 amp/hour Lithiom iron batteries. It charges them from completely dead to full in under 2 hours.
 

Ranger Danger

Member
76
4
8
Location
Vacaville ca
LittleBill
50 amps at 120v = 6000 watts. I'd consider that a hard limit.

We were playing with an MEP802 using my plasma cutter. My plasma cutter is 240V 50 amps. Like clockwork, if we turned it past halfway (25 amps @ 240v) the 802 would drop the load.
This indicates to me that in 240v. it puts out 26 amps TOTAL.
 

LittleBill

New member
20
0
1
Location
Wilkes Barre / PA
That may be where a problem could arise! Its a 50 amp service because to run all or most of the appliances, 26 amps wont cut it! I really need about 25 amps per hot leg!
120 Volt AC Amp Ratings
Appliance or Electronic EquipmentEstimated Amps
Air Conditioner (X number of A/C)12-16 Amps
Blender5-6 Amps
Coffee Maker5-8 Amps
Compact Disc Player1 Amp
Computer (Laptop)2-3 Amps
Converter1-8 Amps
Crock Pot1-2 Amps
Curling Iron<1 Amp
Drill2-6 Amps
Electric Blanket0.5-1.5 Amps
Electric Fan1 Amp
Electric Water Heater9-13 Amps
Electric Skillet6-12 Amps
Hair Dryer5-12 Amps
Iron5-10 Amps
Light (60 watt % 120V)<1 Amp
Microwave8-13 Amps
Microwave (Convection Oven)13 Amps
Refrigerator in AC mode5-8 Amps
Space Heater8-13 Amps
Television1.5-4 Amps
Toaster7-10 Amps
Vacuum (handheld)2-6 Amps
VCR1-2 Amps
Washer/Dryer14-16Amps

12 Volt DC Amp Ratings
Appliance or AccessoryEstimated Amps
Aisle Light1 Amp
CO Detector1 Amp
Fluorescent Light1-2 Amps
Furnace10-12 Amps
LP Gas Leak Detector1 Amp
Overhead lights (Per Bulb)1 Amp
Porch Light1 Amp
Power Roof Vent1.5 Amps
Radio/Stereo4 Amps
Range Hood (Fan & Light)2-3 Amps
Refrigerator (LP Gas Mode)1.5- 2 Amps
Security System1 Amp
Television (12 volt)4-5 Amps
TV Antenna Booster<1 Amp
TV Antenna Booster 12 Volt outletUp to 8 Amps
Variable Speed Ceiling / Vent Fan4 Amps
VCR Recorder / Player2 Amps
Water Pump4 Amp