MEP-003A hook up question

Steel Soldiers is supported by:

wsmolloy

New member
5
0
0
Location
West Palm Beach FL
Maybe wrong thread. I clean the gauge and it appears to constantly hold at about 67HZ. After shutting down it now has no output zero Volts on the meter, zero volts on the lugs. Any thoughts why it would work then 5 minutes later not work?
 

screejunk

Member
48
2
8
Location
Vermont
Keep in mind I do not own a MEP-003a, but do own a smaller 3kw MEP-701a and have skimmed over the MEP-003a TM. First a little basic theory your generator internally is either a 6 or 12 lead reconnectable generator (the distinction does not matter for our purposes here) these leads are reconnected in various combinations by the voltage selector switch by the circuit breaker (never turn this switch with the unit running). In practical terms what this means is your generator can be set to output 120/208V Wye 3 phase power (used in commercial 3 phase equipment), 120V single phase only power or 120/240V split phase (often also called single phase) used in household electrical connections. On the generator power connector you will find screw down split lugs marked L0,L1,L2,L3, in 3 phase mode all 4 connectors are used, in 120V only mode only 2 are used, and in household 120/240 split phase 3 are used (2 lines and a neutral). This is where things start to get confusing because these military generators use a different labeling system than residential 120/240 service with its L0 (neutral), L1 (line), and L2 (line). When the selector switch is in 120/240 mode and you are wanting to connect to a residential system (through a transfer switch for safety reasons) then generator L0 connects to house L0 as neutral, Generator L1 connects to House L1 (line ), then Generator L3 connects to house L2 (line) (note the is L3 to L2). This gives you 120 Volts measured from either line to neutral and 240V measured Line to Line. Measuring these line to line and line to neutral volts and amps is what the selector switch on the CONTROL PANEL does, for single phase operation you will only use some of the possible settings for measurement. At this point you may be asking why have both a 120V only and a 120/240 single phase setting on the voltage selector switch, the answer is in 120V only mode you get access to the full output of the generator, in 120/240V mode the output is split into 2 halves with half the output going to each line output and the return coming back through the neutral, in this mode it is more important to balance your loads and so you never draw more than half the total output out of either line (again back to the use of that meter selector switch on the control panel).


Ike

p.s. another important question when wiring a generator up to a home system is the ground bonding of the neutral connection all the references in the TM will talk about grounding L0 (neutral) to the frame and to a ground rod at the generator for stand alone operation. When used with a transfer switch it may be necessary to unbond L0 at the generator from the frame, or use a transfer switch that has a switched neutral if the MEP003 will not run unbonded. The important thing here is that your neutral is only bonded to ground in 1 place (this is usually at the service entrance for a home) this is a point where you should talk over your plans with your local electrical inspector or other electrical professional as code requirements vary from region to region.
THE "PS" here is important. When you connect a generator to a home via a transfer switch, typically only the two hot lines get transferred from grid to generator or vice versa. The neutral is still connected from generator to panel and to the grid. Since this neutral is already BONDED (i.e. tied to ground) in ONE (and only one) place, you should NOT bond your L0 neutral at generator to the frame and to the grounding rod. You can and should ground the generator frame to a grounding rod via the stud on the frame, but DO NOT bond the L0 neutral to the frame (which is grounded via the grounding rod at the generator).

The key is to understand how your transfer switch works. Does it only transfer the hot load lines (typically two hot lines) or does it transfer both the two hot lines and neutral. In this latter case, you would bond L0 to frame and to the rod at the generator set. Comments welcome as this is the tricky bit where an electrician is worth the $$$.
 

Scoobyshep

Active member
137
70
28
Location
Florida
If you are unsure how to hook to a home safely let me know. I can guide you in the right way of doing it.

Sent from my SM-G950U using Tapatalk
 